[evlatests] Demise of the 'Heat-Pipe' Theory?
Rick Perley
rperley at nrao.edu
Tue Mar 14 18:33:01 EDT 2017
... perhaps we need to outfit one antenna temporarily with some
whopping great fans to stir the air, and equalize the ambient
temperatures for all eight receivers. Then see if the major diurnal
gain effects we see go away ...?
On 03/14/2017 04:19 PM, Wes Grammer wrote:
> The three active He compressors (A, B and D) should be connected as
> follows on all antennas (as far as I know):
>
> A -> (S, Ku, K)
> B -> (C, X, Q)
> D -> (L, Ka)
>
> Given each compressor has a mix of high and low-frequency bands, it
> doesn't seem as likely there's a correlation with supply pressure,
> because you'd expect any LNA gain change to track the cold
> temperatures in a similar fashion, regardless of band.
>
> I do know the upper platform in the Vertex room experiences more
> diurnal temperature variation than down on the floor. Looking at
> yesterday's data on ea17 as an example, it's about 5C for L & S bands
> which are close the floor, while it's ~7-8C for C & X bands and ~11-12
> for Ku, K, Ka and Q bands, which are all up top.
>
> Physical location seems to effect the total temperature change on the
> upper platform as well: the C & X band receivers are basically on one
> side of the platform, while the four higher bands are clustered
> together on the other side.
>
> The post-amps used in the receivers are not the
> temperature-compensated models, to my knowledge, except for the noise
> cal amplifier used in the upgraded receivers with solar Tcals. I don't
> have data on their tempco, but I think I could ask the vendor about this.
>
> -Wes
>
>
> On 3/14/2017 2:45 PM, Steven Myers wrote:
>> by "same cryo" I mean connected to the same compressor, sorry
>>
>> On Mar 14, 2017, at 2:44 PM, Steven Myers wrote:
>>
>>> Are these bands in the same cryo? Do these trends correlate with any
>>> cryo monitoring (return pressure, stage temperatures, etc.)? We used
>>> to see stuff like this in the OVRO 40m due to daily changes in the
>>> compressor output over the course of a day.
>>>
>>> On Mar 14, 2017, at 2:35 PM, Rick Perley wrote:
>>>
>>>> We long ago noted the very large diurnal gain changes seen with
>>>> the EVLA receivers -- particularly at the four high frequency
>>>> bands. Typical power gain changes of 15% are noted, and in some
>>>> cases greater than 20%. These are clearly driven by external
>>>> temperature -- and are expected if the actual temperature of the
>>>> post-amplifiers change by significant -- but plausible -- values.
>>>> It was also noted that the low-frequency bands have similar, but
>>>> considerably smaller (~5%), diurnal variations.
>>>>
>>>> To explain the effect, Bob Hayward posited the 'heat-pipe'
>>>> mechanism: That the horns, being exposed to the cold night air,
>>>> were strongly thermally coupling the external temperature changes
>>>> to the post-amplifiers -- which are mounted with good thermal
>>>> coupling to the horns, and which are known to have a strong
>>>> temperature coefficient.
>>>>
>>>> My recent analysis of data taken on 10/11 February casts some
>>>> significant doubts (at least in my mind) on this theory. I've
>>>> attached eight plots, showing the change in PDif (hence, the change
>>>> in system gain) at the eight cassegrain bands over an 8-hour
>>>> period, starting at 3AM in the morning, and finishing at about
>>>> 11AM, for ea13. This is not a 'specially chosen' antenna (except
>>>> that it is one of only a few for which all switched power data are
>>>> really clean at all bands).
>>>>
>>>> Some points stand out:
>>>>
>>>> 1) The curves are all essentially identical. Most importantly,
>>>> the all maximize at the same time (7AM, local time). There is *no
>>>> lag* between the time of maximum gain and the time of minimum
>>>> temperature at any band.
>>>>
>>>> 2) The four high frequency bands have exactly (to 1%) the same
>>>> gain change -- 15%.
>>>>
>>>> 3) The four low frequency bands also have the same gain change
>>>> -- but at 5%.
>>>>
>>>> If the 'heat-pipe' explanation were the dominant cause, I would
>>>> expect the S and (especially) L band gain maxima to be
>>>> significantly later than that seen at the high frequencies. This is
>>>> not the case. Further, we might expect the X-band and Ku-band gain
>>>> curves to be at least fairly close in amplitude -- since the horns
>>>> are not very different in size. This is also not the case.
>>>>
>>>> Furthermore, the gain changes seen at Q and Ka bands are exactly
>>>> the same as at Ku and K bands. Yet the horns for Q band (and I
>>>> think also for Ka band) do *not* extend outside -- they are
>>>> underneath weather windows. Hence, externally-driven temperature
>>>> changes should be much less at these two highest frequency bands
>>>> than they are for K and Ku bands -- who horns do indeed extend well
>>>> out into the night air. But in fact, they are all the same.
>>>>
>>>> So how is the external temperature changes so strongly
>>>> correlated with the gain changes? And why are the four high
>>>> frequency bands so similar? (And the four low frequency bands also
>>>> similar, but different than the high?) One thing connects all four
>>>> high frequency bands -- the U/X converter. Is it possible that
>>>> this unit -- which is bolted to the side of the receiver cabin --
>>>> is the largest contributor to the observed diurnal effect?
>>>>
>>>> Rick
>>>>
>>>>
>>>>
>>>>
>>>> <13-L.png><13-S.png><13-C.png><13-X.png><13-U.png><13-K.png><13-A.png><13-Q.png>_______________________________________________
>>>>
>>>> evlatests mailing list
>>>> evlatests at listmgr.nrao.edu
>>>> https://listmgr.nrao.edu/mailman/listinfo/evlatests
>>
>> _______________________________________________
>> evlatests mailing list
>> evlatests at listmgr.nrao.edu
>> https://listmgr.nrao.edu/mailman/listinfo/evlatests
>>
>
> _______________________________________________
> evlatests mailing list
> evlatests at listmgr.nrao.edu
> https://listmgr.nrao.edu/mailman/listinfo/evlatests
More information about the evlatests
mailing list