[evlatests] Semi-annual test/inspection of the FM-200 fire suppression system

Gene Cole ecole at nrao.edu
Mon Aug 22 12:14:08 EDT 2011



On 8/22/11 7:40 AM James Sullivan wrote:
> 
> All,
> 
> As a reminder the semi-annual test/inspection of the EVLA Correlator
> room’s FM-200 fire suppression system will be conducted on Wednesday
> August 24th at 9:00 AM.
> 
> The following is a list of the items to be tested and/or inspected, but
> should not be considered complete.
> 
> Test control panels for proper operation.
> Complete function test of all modules.
> Test electrical shunt trip.
> Test the emergency switch over from AC power to battery power.
> Test battery condition (clean cables and connections as needed).
> Inspect all suppression cylinders for proper PSI and agent weight.
> Inspect all nozzles, and piping.
> Visually inspect agent area for unsealed penetrations and room integrity
> Test Ana Laser II system for proper operation.
> Test all smoke detectors, manual releases, rest/abort buttons and any
> other component of the system that falls into the inspection
> requirements of the NFPA.
> 
> 
> Best Regards,
> James B. Sullivan
> NRAO-NM Safety Officer
> Environment, Safety and Security Divisions
> Phone: (505) 835-7344
> 
> 
> 
> 
> 
> 
> 
> 




More information about the evlatests mailing list