Rob Long wrote:
>
> Went to investigate why antenna 24 'died' after a power glitch and
> discovered all four batteries totally dead! Everything in the AC to DC
> power system was working correctly, no fuses were blown, and after
> replacing the batteries, DC power looked fine. I cycled AC power to the
> supply with no problems or drops. I then cycled AC power to the fire
> alarm system which caused the AC contactor to open and kill all AC power
> to the antenna.(Is this functioning properly?)
this is *not* correct...it sounds like a malfunction in the fire
alarm system...the MOS Grp will look at it today...
I think #24 has the new power line monitor installed in the main
AC distribution panel...it could tell us if the power was off for
a couple of hours, but I would think that someone would have noticed
that...
DC power (however)
> stayed stable. Could AC power have been down on antenna 24 for a couple
> of hours? This would have caused the batteries to drain beyond the
> point where the DC contactor could have closed and allowed the batteries
> to recharge. The power seems stable now, so I will keep a close eye on
> 24 for a few days.
>