[Escoordminutes] ES Division Coordination Meeting minutes-June
Lew Serna
lserna at nrao.edu
Wed Jul 1 16:08:00 EDT 2009
Minutes for the ES Division Coordination Meeting held on Tuesday, June
30, 2009, at 10:30 am, in the LL CB conference room. Attending were Lew
Serna, Charley Chavez, Bob Broilo, Gene Cole, Brent Avery, Jim Ruff and
Jon Thunborg.
BUDGET —Budgets are being spent down quickly be sure to monitor your
spending. Stimulus money to the tune of about $5.5M is reported for NRAO
to be spent by 2011. No firm word on how it is being doled out but it is
reportedly earmarked for infrastructure projects. It is likely that some
ES Division items on submitted lists will be funded. We are also
awaiting news from Mark McKinnon on gearbox funding for training, oil
and gears. E-Array project funds are also being sought which will mostly
be contract work but likely some ES Division work will be involved.
PARTS RESTOCKING SERVICES.- The Auto and Track groups are trying out the
automatic restocking by Fastenal. Reports are that the program is
working very well for them. Other groups such as Antenna Mechanics and
HVAC may be interested. Supervisors are asked to provide input on their
groups’ interest.
Surplus Tires—the pile of bad tires is growing. Business division is
looking for a place to take them to because the Socorro dump does not
want to accept them. The cost for disposal of bad tires rests with the
Auto Shop. No action until further notice.
VLBA – The Mauna Kea (09/10/09-09/16/09), and Los Alamos visits remain
for this fiscal year. A Mechanical Visit to Los Alamos is scheduled for
7/14-7/16. Eric has provided Mechanics with a task list for LA.
The Brewster and North Liberty foundations continue to degrade and will
require urgent repairs in the near future at an approximate cost of $15K
each. Foundation work has been placed on the funding wish list and is
expected in FY2010. Work is preferred in the fall not in the winter
since it requires much time to cure.
The pillow block bore dimension of the SC wheel assembly was measured
and is ok. No good reason for the bearing failure can be found.
A check to ensure that the he warehouse has stocked remainder of Wheel
assembly parts necessary to replace all remaining original wheel
assemblies including a spare should be made. HN, MK and KP require one
each assembly to be replaced. The warehouse should stock one set of
parts but no more.
We will continue in FY2010 with Maintenance visits to HN, FD and BR.
Repair of the subreflector brought back from St. Croix is in progress.
Tony has been transferred to track crew so another person has to be
trained to repair. MK dish panels that were damaged were replaced. The
damaged panels will need to be repaired for spares.
A Servo Preload Modification has been designed by Paul Johnson (LA) and
Eric Carlowe for swapping servo preload in order to load the opposite
side of the servo gearbox gears. This should double the life of the
gears in the gearbox. Outfitting of modification will continue on
Maintenance Visits.
It is possible that passports will be required in future visits to St.
Croix.
Some work installing Ka band feeds may be required in the near future.
Guy is checking into using and testing new materials (more affordable)
for making spare dichroic panels.
AZ BEARINGS – Four Bearings were shipped to Rotek for repair. Only 1 of
the four bearings was refurbishable. A second bearing inner race was
touched up and the bearing will be reassembled, usable as an emergency
spare only and has been labeled “emergency spare only”. A third new
bearing is fabricated and shipped. There is a 2 year minimum lead time
for new and refurbished bearings from Rotek.
Antenna 5 bearing and AZ 2 gearbox is changed with Bob Broilo as
supervisor. Bolts for three antennas have been ordered. Older grease
samples show that antennas 25, 10 and 20, are candidates for scheduled
bearing changes. New grease samples of all VLA antennas have been taken.
Antenna 25 has the worst sample and will be in line for replacement in
2010. This is an EVLA antenna. An estimated three weeks in the AAB are
required before a bearing change can occur. Parts from the bearings
removed from antennas are needed for measuring and fitting of new parts
and should be stored until they are scheduled to be shipped for repair.
12 bearings have been replaced to date. It is desirable to order 5 new
bearings before long.
PROJECTS:
CONTROL BUILDING STAIRWAYS— The Control Building Stairways are being
replaced due to their rapid deterioration. The stairways will be
replaced with an improved design conforming to ADA. The western stairway
is complete. A new concrete landing will have to be poured at the base
of the eastern stairway and the steps replaced. The eastern stairway
barricaded to prevent its use. There is no urgency for this project
since safety has declared that there is no need for this stairway as a
means of emergency egress. Work on the eastern stairway will continue as
the workload permits. No further progress.
ST Croix PAINT MAINTENANCE VISIT—It is Apparent that a follow up
painting program should be initiated preferably in the fall. It is
desirable to send a crew to St. Croix to continue painting areas where
bleed through is evident. If this is not possible due to budgetary
constraints, then perhaps the site techs could do the painting for 3
weeks straight with hired help sometime in the fall. Jon will recommend
that Site Techs do spot repairs until enough funds are available for a
follow up painting program.
VLA ANTENNA FOUNDATION MOVEMENT— A problem with north arm antenna
foundation movement needs to be addressed. It appears that the two
rearward station pillars have been slowly separating over the years at
CN6, BN3, CN7 and BN5 with BN5 being the worst. They have separated far
enough in about 33 years that 1 bolt (one on a reward pad) can no longer
be used to secure the antenna pad to the foundation pillar. Modification
of the CN6 plates and BN5 are complete and the plates are reinstalled.
This will solve the immediate problem of setting down antennas on these
foundations.
Markers have been set for taking measurements to try and see which
pillars are actually moving and at what rate. No change has been
observed between loaded and unloaded measurements however better; finer
measurements need to be taken throughout the year.
If the pillars are moving apart it is felt that there may be no
practical way of preventing the movement. It is believed that if this is
the case it would be more desirable/practical to build an additional
foundation next to the bad ones. Another option is that if the pillar
movement is very slow it may be adequate to modify/redesign the mounting
plates in order to make up and correct for the movement. In any case it
would be desirable to get an outside structural firm to inspect the
foundations and make a recommendation.
GENERATOR REPAIRS— Minor leaks were noticed at the engine rear seals and
it is desirable to install a better fuel filtering system. A bearing on
the generator unit also should be replacement as a PM. This work would
cost around $15K and has been put on the funding wish list.
HOT WATER LOOP. A project is submitted to install a hot water loop using
Correlator waste heat: The difference between the summer load and winter
load is mostly due
to heating (at least 300kW). However, even during the coldest mornings
the cooling tower is ventilating correlator waste heat into the
atmosphere. We already use some of the heat in the Control Building, but
by extending the hot water loop to other buildings, we may be able to
reduce our power demand. The WIDAR correlator will have an even higher
heat output to work with.
This project mainly consists of burying a hot water loop and using heat
exchangers similar to what many complexes of buildings use. Payback on
this project could be as quick as 1 year. Bob Broilo will investigate
and provide further information. No progress..
125vdc GENERATOR SUPPLY MODIFICATION. A safety switch and other related
wiring changes to the VLA Standby Generator Battery supply have been
completed in order to make servicing the batteries a safer operation and
without interruption of the battery supply to the generator system
controls. New safety procedures and training will have to be provided to
personnel who service the batteries. This project is complete.
VLA AZ GEARBOX’s (Antenna 5 etc..)--Antenna 5’s #2 gearbox experienced a
catastrophic failure failed on Wednesday, April 15, 2009. Antenna 5 #1
gearbox was ok. We replaced the bad gearbox with the spare gearbox. The
bad gearbox is salvageable and will be repaired. Several gears will be
fabricated in a shop out of Carlsbad, NM for around $800ea.
VLA Az Gearboxes are due for oil changes. A plan to change around 10
antennas per year is being formulated beginning with remaining 6 VLA
antennas and then continuing with all EVLA antennas @ approx. 10/ year.
Training and equipment will be required. Guy Stanzione will be in charge
of preparing for the gearbox inspections, training & repairs.
VLA FRM—One VLA FRM focus ring gear was damaged last year. The spare FRM
was cannibalized in order to repair the Antenna. A new ring has been
ordered for repairing the cannibalized spare at a cost of $3K and should
arrive soon. FRM inspections will resume during the next antenna
overhaul cycle to check for possible FRM overhaul tasks.
BALLAST DOORS-- New project is proposed to convert manual opening of
ballast car doors to hydraulic controlled opening of the doors for
dispensing ballast from the cars. Much dust is created and the operator
is too close to the doors to be able to observe the dispensing properly
and safely. This Project will cost around $8K.
EVLA;
Civil— Correlator Room: The Air Conditioning system needs to be tied in
to the CPCC for controlling of air handlers when desirable and during
emergency shutdowns. ESD monitoring equipment is installed on the door
closest to Ops, to be used prior to entering the shielded Correlator
room. For controlling traffic to the correlator, a special one way door
will be installed at the end of the elevator hallway. It will be used
for exiting the correlator area only but will be capable of being
propped open for passing equipment through if necessary. The doors are
in and will be installed next week.
Safety has scheduled fire alarm testing with Operations on August 25,
2009. Bob will coordinate that effort with the annual battery maintenance.
EVLA Antennas—The Antenna Group must complete mechanical overhauls to 23
antennas to meet the retrofit schedule for EVLA design in FY2009. This
goal is currently on schedule
A total of 20 S-band (2-4 GHz) feed horns will be fabricated in FY2009.
S-band feeds are assembled so far. All rings have been cut for the
S-band. The Ku-band (12-18 GHz) feed horns will also be fabricated in
FY2009. This is on schedule.
A prototype insulating of the feed cone/vertex room is done in EVLA
antenna 25 in an effort to improve temperature stability in the feed
cone/vertex room. Bob has used a thermal imager to see where we are
losing most of the heat in the feed cone. An analysis and recommendation
will be made as soon as time permits.
Antennas will remain in the D array for 7 months.
As antenna #7 goes on line it is desirable to replace some of the early
EVLA antennas with newer version EVLA antennas. Older versions will
begin to be decommissioned (since the VLA Correlator cannot operate more
than 22 antennas) for upgrades in the field. There will also be a period
of 2 months (Jan. & Feb.) that there will be no observing due to the
Correlator being shutdown . This is an opportunity to bring older
antennas up to date.
SAFETY REPORT: No Safety Officer present
Safety Manager, Bob Daniels will visit the VLA on July 13. Training on
Hazard recognition and mitigation is forthcoming. Training on Arc Flash
protection.
ANNOUNCEMENTS:
ETK Training (Electronic Timekeeping) Electronic Timekeeping—— For
/exempt/ staff members, we are requiring that you utilize /both/ the ETK
system and the paper timesheets beginning with the current pay period
April 21^st through May 20^th . All NRAO /non-exempt/ staff members are
required to utilize /both/ the ETK system and paper timesheets until
further notice. /Supervisors/ will approve the paper timesheets as usual
but will also approve all ETK entries at the end of the pay periods.
* *
*2008 PERFORMANCE EVALUATION PROCESS *
*June 30 Appraisal Forms Completed *– Supervisor reviews completed
performance appraisal forms with division head and receives approval.
Supervisor begins scheduling and holding evaluation meetings with
employees.
*June 17 Employee Meetings Concluded *– All evaluation meetings to be
concluded and appraisal forms signed by the employee. Employees should
be given sufficient time (at least 24 hours) to review and comment on
the evaluation. Based on information provided by the employee,
supervisors should make corrections and changes as appropriate.
*July 31 All Forms Delivered to HR *– All of the original completed and
signed appraisal forms must be forwarded to the appropriate Human
Resources Office. A copy of the signed appraisal should be provided to
the employee